electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Apr 12, 2004 #1 I have to run some No. 16 control wiring between equipment in 1? EMT. I have some type TFFN already. Can I use it for this application? Thanks
I have to run some No. 16 control wiring between equipment in 1? EMT. I have some type TFFN already. Can I use it for this application? Thanks
R rhombus65 Member Apr 12, 2004 #2 Re: Wire Type Based on my knowledge of TFFN there is no reason why you could not use it. If you would be able to use # 16 THHN than TFFN is fine. It is supposed to be more resistant to physical abuse.
Re: Wire Type Based on my knowledge of TFFN there is no reason why you could not use it. If you would be able to use # 16 THHN than TFFN is fine. It is supposed to be more resistant to physical abuse.
hbiss EC, New York NEC: 2017 Location Little Falls, New York NEC: 2017 Occupation EC Apr 12, 2004 #3 Re: Wire Type Sure, no problem. TFFN in raceway is a Class 1 wiring method. We do it all the time. -Hal
Re: Wire Type Sure, no problem. TFFN in raceway is a Class 1 wiring method. We do it all the time. -Hal
electricman2 Senior Member Location North Carolina Occupation Retired Electrical Contractor Apr 12, 2004 #4 Re: Wire Type Thanks all. Since it was listed in table 402.3 as fixture wire, I wasn't sure if it could be run in a raceway as control wiring.
Re: Wire Type Thanks all. Since it was listed in table 402.3 as fixture wire, I wasn't sure if it could be run in a raceway as control wiring.