JohnJ0906 said:If the door knocks at 3 AM, it's Copper.org. They wish to have a "word" with you.
They tried that with me once. I chased them away using a whip made from 14/2 NM cable.
JohnJ0906 said:If the door knocks at 3 AM, it's Copper.org. They wish to have a "word" with you.
Same here. I follow my own advice when I build for myself. I use #14 on lighting circuits and #12 on receptacle circuits, even in bedrooms, living rooms, etc.iwire said:Both, 12 where required 14 where it's allowed and I have been re-wiring my home.Podagrower said:With all that being said, if it was your house, would you use 14 or 12 for the branch circuits?
LarryFine said:Same here. I follow my own advice when I build for myself. I use #14 on lighting circuits and #12 on receptacle circuits, even in bedrooms, living rooms, etc.
Lighting loads are relatively predictable; receptacle loads aren't. Plus, when many people vacuum is when they're most likely to turn on all of the lights in a room.
It's not just the 600 watts. In a typical small 3-bedroom house, I might place all of the lighting for the 3 bderooms, closets, bath(s), and hall on a single 15a circuit, and the receptacles (bedrooms and hall, not bath) on a single 20a circuit.stickboy1375 said:Sorry Larry, I've never had a call back for a vacuum tripping a breaker, IMO # 12 is a complete waste for general purpose receptacles. All I'm saying is # 14 is fine and so is # 12, I just dont see the point in running # 12 for an extra 600 watts.
LarryFine said:Oh, I have seen vacuums cause 15a circuits to trip, and the lights do go out.
iwire said:OMG No! .......
I have two 20 amp circuits in my kitchen, the wife still tripped them as she insisted in plugging a large electric fry plate in to the same duplex as the convection oven. She knows how to reset the breaker. :smile:
cschmid said:But I do not believe with I can justify a 15amp convince receptacle at all..with the increased demand for electric gadgets more and more items are being plugged in..we are a hard wired society..
cschmid said:man you guys are on copper.org..
Lxnxjxhx said:The average midwest person uses 800 watts, continuously.
1 kW is probably more representative.
How many people in the average house?
1000' of #12 at 5 A dissipates 40 watts.
1000' of #14 at 5 A dissipates 63 watts.
How many feet of wire in a house?
peter d said:Only because they are one of the biggest offenders for promoting the "#12 is better in residential" myths, among others...
cschmid said:Now back to copper org. just because they say it is does not mean it is so..
don_resqcapt19 said:The watt loss calculation for #12 v #14 is flawed. It assumes that all of the current is on a single circuit.
His use of five amps is almost the total average load of 800 watts that he cited. It is not likely that this average load is on a single circuit. It would be on multiple circuits and because the watt loss on each conductor is a function of the current squared times the resistance, a drop in current makes a huge difference in the line losses.iwire said:He used 5 amps as the load, it would be very likely that 5 amps was being used at a single receptacle. Obviously if you divided that 5 amps across two 14 AWG circuits the loss will be less.
BryanMD said:The uses that resi recepticles are applied to today are VERY different than what they were asked to do even 20 years ago.
Every room has electronic devices and other appliances permanantly plugged in that in addittion to constantly sucking power would be at best inconvenient to have a power loss by tripping a breaker.
TV's and computers are at the top of this list.
Independent of amp draw is the sheer number of them.
KNOWING that almost every kids bedroom today will have (in addition to the table lamp and clock radio we may have had) a CRT and tower and printer and 19" color TV and DVD player and game Console and stereo system, etc. i
It is prudent at least for whoever is going to live there to SPECIFY that the number of recepticles and the circuits supplying them be sufficent in number but also sufficient in independence from what may be happening in the next (similarly loaded) room down the hall.
This goes beyond whether those circuits are fed by 14 or 12 wire.
Code minimum isn't enough anymore. And it isn't enough in the low priced tract house as much as it isn't enough in the Mcmansion.