B butch5 Member Feb 16, 2004 #1 I was told that i could not run wire through the 2x4 stringers in new construction. The home owner wants to use the attic space for storage. How do i run the wiring for the bedroom and bath lights.
I was told that i could not run wire through the 2x4 stringers in new construction. The home owner wants to use the attic space for storage. How do i run the wiring for the bedroom and bath lights.
ryan_618 Senior Member Location Salt Lake City, Utah Feb 16, 2004 #2 Re: Wireing in 2x4 stringers What is a 2x4 stringer?
B butch5 Member Feb 16, 2004 #3 Re: Wireing in 2x4 stringers A stringer is used to support a floor or roof.
ryan_618 Senior Member Location Salt Lake City, Utah Feb 16, 2004 #4 Re: Wireing in 2x4 stringers It sounds to me like you are talking about a purlin that is used to break the span of a rafter. Is your concern drilling through structural members?
Re: Wireing in 2x4 stringers It sounds to me like you are talking about a purlin that is used to break the span of a rafter. Is your concern drilling through structural members?
wanderer20001us Senior Member Feb 16, 2004 #5 Re: Wireing in 2x4 stringers I hope they're not use 2 x 4 floor stringers.
B butch5 Member Feb 16, 2004 #6 Re: Wireing in 2x4 stringers My mistake. Yes i need to drill through the purlin.
ryan_618 Senior Member Location Salt Lake City, Utah Feb 16, 2004 #7 Re: Wireing in 2x4 stringers I see no problem with drilling a purlin, as long as it is less than 40% of the width of the stud, and no closer than 5/8" to the edge.
Re: Wireing in 2x4 stringers I see no problem with drilling a purlin, as long as it is less than 40% of the width of the stud, and no closer than 5/8" to the edge.
B butch5 Member Feb 16, 2004 #8 Re: Wireing in 2x4 stringers That,s what i thought,so i should not have to worry about the shear strength of the 2x4 then?
Re: Wireing in 2x4 stringers That,s what i thought,so i should not have to worry about the shear strength of the 2x4 then?
ryan_618 Senior Member Location Salt Lake City, Utah Feb 16, 2004 #9 Re: Wireing in 2x4 stringers No. You should be fine.
ryan_618 Senior Member Location Salt Lake City, Utah Feb 16, 2004 #11 Re: Wireing in 2x4 stringers Any time