Is it permissible to run the line and load wires in the same conduit from the disconnect to a trough and then to the motor. any input is appreciated
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: wireing motor disconnects

Yes it is. Think of a light switch drop where feed and switchleg are in the same conduit.

Where this wouldn't be allowed would be in the case of a service, see 230.7

Roger
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: wireing motor disconnects

Sounds like you would have more than 3 current-carrying conductors in the same conduit. If so, don't forget to derate the ampacity of the conductors.
 