wireing motor disconnects

Status
Not open for further replies.

bwb48us

Member
Location
Pennsylvania
Is it permissible to run the line and load wires in the same conduit from the disconnect to a trough and then to the motor. any input is appreciated
 
Re: wireing motor disconnects

Yes it is. Think of a light switch drop where feed and switchleg are in the same conduit.

Where this wouldn't be allowed would be in the case of a service, see 230.7

Roger
 
Re: wireing motor disconnects

Sounds like you would have more than 3 current-carrying conductors in the same conduit. If so, don't forget to derate the ampacity of the conductors.
 
Status
Not open for further replies.
Top