is it in the code book that you cannot run wires between the framing and the concret wall in a finished basement. the wires were stapled as support every 2ft
 
As long as the wires are properly supported and not subject to physical damage I see no problem with this.

Chris
 
raider1 said:
As long as the wires are properly supported and not subject to physical damage I see no problem with this.

Chris
I agree with the notorious post hijacker, Chris. :grin:

Edit to add

I will go so far as to say you can fasten NM to the block wall.
 
Dennis Alwon said:
I agree with the notorious post hijacker, Chris. :grin:

Edit to add

I will go so far as to say you can fasten NM to the block wall.

Shhhhh! If it gets out that I am a post hijacker I will be on every government watch list and never be able to fly again!:D

Chris
 
raider1 said:
Shhhhh! If it gets out that I am a post hijacker I will be on every government watch list and never be able to fly again!:D

Chris

This is going to cost you. :D

stacks%20of%20money.jpg
 
raider1 said:
All I have on me is some pocket lint and a breath mint.:D

Chris

Your fellow workers will kill me if I take the breath mint and being I am not into pocket lint I will let it slide this time. :D
 
You mean like this?

BasementNMbehindframing.jpg

Unless it's right next to the box, I don't staple the NM directly. I just use scrap sheathing.

BasementNMbehindframing2.jpg
 
480sparky said:
You mean like this?

Unless it's right next to the box, I don't staple the NM directly. I just use scrap sheathing.



Is that sheathing listed for the purpose and how many wires can you legally secure with it????:D
 
I like that sheathing method. It looks better then bending the wire at every joice to get a staple in it.

I have also used 3/8 one hole straps to fasten it to the concrete.
Never been called on it.
 
Dennis Alwon said:
Is that sheathing listed for the purpose and how many wires can you legally secure with it????:D

How many cables can I put through a hole in a 2x4, and is it listed for that purpose?
 
buckofdurham said:
I like that sheathing method. It looks better then bending the wire at every joice to get a staple in it.

I have also used 3/8 one hole straps to fasten it to the concrete.
Never been called on it.


NM only requires strapping every 4.5' so it wouldn't require support at every joist. You could use the jacket method for intermediate support since it wouldn't be required in the first place. I agree it can't be used as a replacement for other methods such as staples, stacker's, etc.

Are 3/8" one hole straps listed for flat NM cables? We always use the special flat NM style straps when strapping to a wall.
 
480sparky said:
How many cables can I put through a hole in a 2x4, and is it listed for that purpose?

The 08 code covers that belive it or not.
Somebody will correct me but I think it's two.

At the same time the 08 code wants us to drill the joices in a crawl space.
No more stapling along the bottom of the joices:D :mad:
 
infinity said:
Are 3/8" one hole straps listed for flat NM cables? We always use the special flat NM style straps when strapping to a wall.

No their not listed, But don't tell our local ahj's.
I have seen the flat one wholes for big wire.
I've not seen any for 12 or 14,, I will have to look for them.
Probably has the edges more rounded so as not to damage the wire.
 
Last edited by a moderator:
Another method for supporting NM cable installed in these areas is to drill a hole in every second or third stud and run the NM cable through those holes.

Dennis Alwon said:
Your fellow workers will kill me if I take the breath mint and being I am not into pocket lint I will let it slide this time.

My co-workers and wife thank you.:)

Chris
 
480sparky said:
You mean like this?

BasementNMbehindframing.jpg

Unless it's right next to the box, I don't staple the NM directly. I just use scrap sheathing.

BasementNMbehindframing2.jpg



Seems like just drilling some holes would be faster
 