Trawets
Member
- Location
- Pittsburgh
I have 4 electric salamander heaters that are permanently installed on walls at my work. 2 are fed from one panel and 480/208 transformer and the other 2 are on a separate floor with its own panel and transformer. All 4 are wired in a similar fashion and are suffering from the same issue. The problem is the conductor insulation is melting at the disconnects on the line side and the breaker and wires are overheating (120 F +).
Here's the setup working from heater to breaker panel:
3 phase, 208 Dayton model 1RKT9 heater, 42 amps
5' to 10' of 6/4 SO cord
60 amp Siemens non-fused disconnect, cat # GNF322
150' of #6 THHN copper inside 1"emt (3 hots, 1 ground) ran in plenum drop ceiling
3 pole, 208 v, 60 amp Square D bolt on breaker
All terminations are 60/75 degree rated
voltage at panel is 215
voltage at disconnect is 211 while running
amp draw is A 41, B 41, C 39 (I think the fan is single phase)
I have no loose connections and I think all my calculations are correct. I plan on up-sizing the wire to #4 and replacing the breakers but that still has me scratching my head as to where I went wrong. Any help is appreciated!
Just to be clear, the 480/208 transformer is configured for a 208 Delta secondary, and the heaters are wired line to line with no neutral? That is why the fan current appears on only two lines?
Here's the setup working from heater to breaker panel:
3 phase, 208 Dayton model 1RKT9 heater, 42 amps
5' to 10' of 6/4 SO cord
60 amp Siemens non-fused disconnect, cat # GNF322
150' of #6 THHN copper inside 1"emt (3 hots, 1 ground) ran in plenum drop ceiling
3 pole, 208 v, 60 amp Square D bolt on breaker
All terminations are 60/75 degree rated
voltage at panel is 215
voltage at disconnect is 211 while running
amp draw is A 41, B 41, C 39 (I think the fan is single phase)
I have no loose connections and I think all my calculations are correct. I plan on up-sizing the wire to #4 and replacing the breakers but that still has me scratching my head as to where I went wrong. Any help is appreciated!
Just to be clear, the 480/208 transformer is configured for a 208 Delta secondary, and the heaters are wired line to line with no neutral? That is why the fan current appears on only two lines?