376.22(B)
The adjustment factors 310.15(B)(3)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions 310.15(B)(5), exceeds 30 at any cross-section of the wire way.
My question:
When you hit that magical number of 31 CCC's, do you just derate counting the number of CCC's over 30 or would you start derate all of the conductors?
So if you have 32 CCC's in the wireway, would the derating be based on 2 CCC's or 32 CCC's?
The adjustment factors 310.15(B)(3)(a) shall be applied only where the number of current-carrying conductors, including neutral conductors classified as current-carrying under the provisions 310.15(B)(5), exceeds 30 at any cross-section of the wire way.
My question:
When you hit that magical number of 31 CCC's, do you just derate counting the number of CCC's over 30 or would you start derate all of the conductors?
So if you have 32 CCC's in the wireway, would the derating be based on 2 CCC's or 32 CCC's?