I have a wireway with more than 41 Current carrying conductors (but less than the 20% fill by cross sectional area). One of the loads is a 40HP fan drawing 52 Amps. Assuming an ambient temperature of 30?C (86?F), I have calculated that a #1 cable would be required (#1 THHN at 90?C (194?F) is rated at 150 Amps multiplied by 35 percent = 52.5 Amps) Is this correct? It would appear that significantly larger conductors are required when using a wireway as opposed to an individual conduit. Does this not largely offset the advantages of using a wireway?