Need help sizing a gutter/wireway for building service with the following:
1 - 1600 amp main disconnect with 4 parallel runs of 4# 600 MCM and 1 # 4/0 THHN CU conductors in 3.5" conduit. Conduits will leave top of disconnect and enter bottom of gutter. Gutter/wireway will then extend over four 200-amp unit meters and two 400-amp unit meters. Length is no problem to figure, but what width and depth is required? Engineer has the notoriuos "Sized per NEC" note for this gutter/wireway.
Thanks,
1 - 1600 amp main disconnect with 4 parallel runs of 4# 600 MCM and 1 # 4/0 THHN CU conductors in 3.5" conduit. Conduits will leave top of disconnect and enter bottom of gutter. Gutter/wireway will then extend over four 200-amp unit meters and two 400-amp unit meters. Length is no problem to figure, but what width and depth is required? Engineer has the notoriuos "Sized per NEC" note for this gutter/wireway.