Tonuch
Member
- Location
- Medford, NJ, USA
First I would like to thank the community for participating in this forum I use it all the time but this is my first tome posting a question. I have an installation with a 42 circuit panel over top of which I have mounted a 24”long by 12” wide by 12” deep trough(wireway or junction box) , coming out of bottom of trough are three 2” conduits that are 22” long and enter the the top of the panel. I have 38 12/2 mc cables coming into top of trough (for a total of 76 ccc) and travel through the trough unbroken into the panel. The ahj is citing a violation, in that if we exceed 30 ccc in a wireway we must derate. My question is “what is the difference between a wireway and a junction box and if there are different requirements for junction boxes as opposed to wireways in regard to derating in a installation like mine”