TwistLock
Member
- Location
- California
- Occupation
- Electrician
I used this image mock up for a pre-inspection to make sure inspector was onboard with it. He didn’t have any issues but he also couldn’t guarantee he would be the one coming for final. (He was fine with blocking vent).
My question is if the 10x10x6 Nema 3R is ok with this many ‘spliced’ conductors or is it a wire-way subject to derating because more than 30ccc’s.
I would be feeding the Junction box with a ≤ 24” piece of 2” EMT. I’m assume 60% fill because of this and zero derating for this section. Rain-Tight listed fitting into top of Nema 3R.
If this is allowed I just thought it would be easier than torturing multiple conduits due to KO layout on bottom of panel. Inspector also said he did not consider area below panel to be subject to physical damage fwiw.

My question is if the 10x10x6 Nema 3R is ok with this many ‘spliced’ conductors or is it a wire-way subject to derating because more than 30ccc’s.
I would be feeding the Junction box with a ≤ 24” piece of 2” EMT. I’m assume 60% fill because of this and zero derating for this section. Rain-Tight listed fitting into top of Nema 3R.
If this is allowed I just thought it would be easier than torturing multiple conduits due to KO layout on bottom of panel. Inspector also said he did not consider area below panel to be subject to physical damage fwiw.