Twoskinsoneman
Senior Member
- Location
- West Virginia, USA NEC: 2020
- Occupation
- Facility Senior Electrician
Which of these illustrations is accurate?
Also the section seems to imply that increase for additional entries should apply to the distance from opposite wall AND distance between raceways...
What say ye?!
314.28(A)(2)
(2) Angle or U Pulls or Splices. Where splices or where
angle or U pulls are made, the distance between each raceway
entry inside the box and the opposite wall of the box
shall not be less than six times the metric designator (trade
size) of the largest raceway in a row. This distance shall be
increased for additional entries by the amount of the sum of
the diameters of all other raceway entries in the same row
on the same wall of the box. Each row shall be calculated
individually, and the single row that provides the maximum
distance shall be used.
Also the section seems to imply that increase for additional entries should apply to the distance from opposite wall AND distance between raceways...
What say ye?!
314.28(A)(2)
(2) Angle or U Pulls or Splices. Where splices or where
angle or U pulls are made, the distance between each raceway
entry inside the box and the opposite wall of the box
shall not be less than six times the metric designator (trade
size) of the largest raceway in a row. This distance shall be
increased for additional entries by the amount of the sum of
the diameters of all other raceway entries in the same row
on the same wall of the box. Each row shall be calculated
individually, and the single row that provides the maximum
distance shall be used.