Hi. I am an engineer in the UK looking to design a control system for a customer in the US but I am having some difficulty with the use of wireways with regard to fill and de rating. The customer has specified the use of NEMA 12 wireway which is fine but when I read up on the NEC guidelines things start to worry me?
I have a control panel supplying numerous motors and supplies on a machine. My largest supply requirement is 32A. Now I would typically use multicore cables, 3c+E, 5c+E etc to wire the supplies directly from the control panel but everything I read makes reference to single cores?
Is it common practice in the US to wire machines in single core cables away from the control panel?
Are multicore cables used in this way and wired in wireway?
How are multicores perceived in this situation, I think I have read somewhere that a multicore is treated as a single cable, is this correct and if so how is this taken into account as far as de rating and fill?
For example if the multicores are seen as single cables then i will have in excess of 40 which then means a de rating of 35% if I am not mistaken. This would mean that my 6mm square cable for my 32A supply has now increased to a 90mm square cable?
Any feedback would be appreciated.
Thanks
Thanks