I think I already know the answer here but I want to hear it from the Code gods on the Forum before moving forward.
Does the 30 current carrying ‘conductors’ only apply to single conductors or does it also apply to multi conductors? Say I have 10, 3/C multi conductor branch circuits feeding 10, 3 phase motors does this constitute 30 current carrying conductors or just 10?
And if none of the motors meet the definition of continuous load, would this allow for a higher number of conductors before adjustment factors apply?