I was asked the question whether a polaris type of connector can be installed in the above enclosures.. An inspector thought he remembered reading that the terminations had to be mounted to the enclosures.

I cannot find anything in those sections that would disallow a polaris type splice. Anyone know something different. I seem to remember this coming up before but I am so forgetful who knows what I am remembering.
 
See section 376.56(B) on power distribution blocks. And you are right it does not say it has to fastened, interesting.
 