We are planning on installing weatherproof wireways outside the residential building against the exterior wall. There will be 120/208V feeders inside the wireways. Is there anything in the code that says how many feet it should be away from the windows?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
There is a common misconception concerning clearances based on 230.9 but that Section refers to "open conductors"
 