yes, this unit has a 30 and a 60 on it already...it has a bonding strap if you choose to run one feeder or you can remove it to use two wires

Then it is fine.
Because the controll wiring must be wired to both strips.
So when the sensors click off. One strip and or the other will go off.
 
There is nothing wrong with this instalation. You can put #6 romex on a 60a and #10 on a 30a breaker all day long. I would do it this way if I already had the wire.

put #6 Romex on a 60 amp breaker with a load over 55 amps and you will get a red tag in this area.
 
You can go to the next standard size.

Got a code number ? Or this just what the boys want there ?



You can not use 240.4 to bump up to a 60A breaker if the calculated load exceeds the 55A that the wire is good for. This comment is from NEC Plus website commentary to 240.4:

" For circuits rated 600 volts and under, the allowable ampacity of branch circuit, feeder, or service conductors always has to be capable of supplying the calculated load in accordance with the requirements of 210.19(A)(1), 215.2(A)(1), and 230.42(A).
 
You can not use 240.4 to bump up to a 60A breaker if the calculated load exceeds the 55A that the wire is good for. This comment is from NEC Plus website commentary to 240.4:

" For circuits rated 600 volts and under, the allowable ampacity of branch circuit, feeder, or service conductors always has to be capable of supplying the calculated load in accordance with the requirements of 210.19(A)(1), 215.2(A)(1), and 230.42(A).

well, its a 10 kw load, so i dont htink theres a problem
 
They don't make a 55a breaker check 240.6

true, but 310 lsits the ampaciy of the conductor.
240.6 allows you to go to the next standard OCP device, but does not permit you to exceed the conductor's ampacity.
 