It looks as if it comes with a factory cord with a 20 amp 230v plug, but the internals come set up for 120v.
I wonder if that 6 amp draw is at 230v or 115?
I would install receptacles to match the cord (to avoid changing all those cord caps) but you might have to change each unit to 230v internally.
Do you have a number for a manufacturer tech?
There's a disaster waiting to happen.[/list]
It looks as if it comes with a factory cord with a 20 amp 230v plug, but the internals come set up for 120v.
Unless each machine requires its own circuit anyway, wiring them for 240v would allow three per circuit, instead of one per 120v circuitI was able to speak to a tech and he was quite helpful, he said that using 120V the unit draws 10A.
There's a disaster waiting to happen.