- Location
- Bremerton, Washington
- Occupation
- Master Electrician
Use the IMC as your EGC. At the motor, use LTFMC, and get the connectors that have the external bonding lugs, and run 4 AWG. T&B makes these connectors. I had a 50 hp motor wired in 1" RMC with 3 4AWG THN, which was never going to come out as it went waaay in the back of an MCC. So I used the T&B LTFMC connectors with an external bond wire (max 6 ft). There is a picture of this install in Mike Holts Grounding and Bonding text. Later I can post a picture.