Pierre C Belarge
Senior Member
- Location
- Westchester County, New York
buck33k said:I'd say a problem with 312.5(C) as the cables are not secured to the cabinet. Also, has derating been considered per 376.22.
I agree with this.
312.5(C) Cables.
where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
There is the exception to this section, and there are multiple conditions of which "ALL of the following conditions are met"
I do not see all of the conditions listed in the exception as being followe.
Also it was mentioned about the bonding of the trough, or the lack of bonding of the trough.
Otherwise, it is a clever attempt at trying to install an aesthetic method for NM cable.