An inground pool will have two motors and an ionizer.
I'm directed to an existing garage panel..
the panel is older GE fed main lug with 9 single pole breakers in it..
I'm thinking it should have a main breaker installed and to add a couple of ground rods.
The feeder is 6's and a 10 thru 1"pvc..
the 10 grd and 6 neutral are together on the neutral bar which will need to be separated..
At the main panel, the feeder is #6 AC I think??
The inside of the panel at the connector looks to be more of a rigid pipe entry and not an AC (bx) connector??? there is no ground conductor, everything is sheet-rocked around the panel and basement..
There was a small opening for the H2O meter That I was able to shine some light up at that part of the outside of the panel.. again, I'm guessing it's AC.
The basement is closed in with sheetrock...I can't locate the conduit where it leaves the building to go out to the garage. It looks like the building has had two additions added toward the garage, maybe the existing foundation before the first or second foundation has the garage feed conduit?
Either way, I removed the 10 thhn at the garage and checked for voltage phase to that ground and get the 120v so guessing and hoping someone did the right thing where the bx(?) and the pvc are spliced.
The question.
I looked at the ucc for jersey and I believe we are under the 2011 code.
nec 2011
680.25(A)(1) exception says existing feeder to panelboard to be run in flexible metal conduit or an approved cable assembly that includes an equipment ground conductor within the outer sheath. (2014 states insulated ground conductor)
Is that saying flexible metal conduit (AC) is one option, and cable assembly with a ground conductor is another option.
OR
Is that saying that the FMC needs a ground conductor and also the cable assembly needs a ground conductor?
Thank you..
Happy Memorial Day
I'm directed to an existing garage panel..
the panel is older GE fed main lug with 9 single pole breakers in it..
I'm thinking it should have a main breaker installed and to add a couple of ground rods.
The feeder is 6's and a 10 thru 1"pvc..
the 10 grd and 6 neutral are together on the neutral bar which will need to be separated..
At the main panel, the feeder is #6 AC I think??
The inside of the panel at the connector looks to be more of a rigid pipe entry and not an AC (bx) connector??? there is no ground conductor, everything is sheet-rocked around the panel and basement..
There was a small opening for the H2O meter That I was able to shine some light up at that part of the outside of the panel.. again, I'm guessing it's AC.
The basement is closed in with sheetrock...I can't locate the conduit where it leaves the building to go out to the garage. It looks like the building has had two additions added toward the garage, maybe the existing foundation before the first or second foundation has the garage feed conduit?
Either way, I removed the 10 thhn at the garage and checked for voltage phase to that ground and get the 120v so guessing and hoping someone did the right thing where the bx(?) and the pvc are spliced.
The question.
I looked at the ucc for jersey and I believe we are under the 2011 code.
nec 2011
680.25(A)(1) exception says existing feeder to panelboard to be run in flexible metal conduit or an approved cable assembly that includes an equipment ground conductor within the outer sheath. (2014 states insulated ground conductor)
Is that saying flexible metal conduit (AC) is one option, and cable assembly with a ground conductor is another option.
OR
Is that saying that the FMC needs a ground conductor and also the cable assembly needs a ground conductor?
Thank you..
Happy Memorial Day