In case it isn't obvious from the 680.25 postings, you get no relief from conduit when in or on a house. With pool branch circuits yes, feeders no. So you can use SER in the house, but it must be within conduit, and I'd argue this would need to be a complete conduit system so huge conduit will be needed to take a SER cable as if it was a giant single conductor.
The only way to use SER without conduit is if was as existing feeder.
I think you'd be better off to run conduit from the house panel to the pool panel and just run four individual conductors through that conduit. Make sure to use a W rated wire (e.g. THWN, RHW, XHHW).
Is the #8 you keep mentioning the equipotential bonding grid wire or the equipment ground for the feeder? If it is the equipotential bonding wire, it does not connect to any panelboard -- it just interconnects everything near or to plumbed to the pool.
The only way to use SER without conduit is if was as existing feeder.
I think you'd be better off to run conduit from the house panel to the pool panel and just run four individual conductors through that conduit. Make sure to use a W rated wire (e.g. THWN, RHW, XHHW).
Is the #8 you keep mentioning the equipotential bonding grid wire or the equipment ground for the feeder? If it is the equipotential bonding wire, it does not connect to any panelboard -- it just interconnects everything near or to plumbed to the pool.