sparkync
Senior Member
- Location
- North Carolina
When figuring the feeder size to pool pumps and equipment, I know that I take the largest motor at 125% and then add the FLA of the other motors, but do I take the 115v FLA or the 240v FLA if the motor is dual voltage? I thought I read somewhere in the code that you have to figure it ( the feeder, not branch circuit ) for the higher amperage even though it's not going to be used at the time. A feeder has already been pulled for a hot tub, and it was supposed to be big enough to feed the pool, but I don't think it is at this point. I have to do some more checking. It looks like they have pulled #6 wire (or # 4 at the most), to a 4 circuit wp panel. They have a 60amp. GFI breaker feeding the hot tub. I will have to look and see what the hot tub actually calls for, and the size of motor it has. I'm guessing it will be the largest motor of the group and that I will have to figure it at 125% then the others at 100%FLA, but whether I take it at 115v or 240v is my question. Thanks for the help...Steve
Problem here is that if I have to pull another feeder, I will be coming out of the panel in their house, under a 10 or 12 ft. asphalt driveway then about 100ft. to the pool panel