wiring question

Status
Not open for further replies.

Designer69

Senior Member
Pls see attached pic.

Is this how an electrician would wire this circuit where it's desired to control an additional lighting ckt. from existing ltg. switch via contactor?


Thank You cont wir.jpg
 

MAC702

Senior Member
Location
Clark County, NV
Looks like it would work to me.

Please be a lot more specific in the subject line. Half of our threads are 'wiring questions.'

"Can I add a ltg contactor to the load side of a 3-way switch system?" would be a great subject line.
 

kwired

Electron manager
Location
NE Nebraska
Pls see attached pic.

Is this how an electrician would wire this circuit where it's desired to control an additional lighting ckt. from existing ltg. switch via contactor?


Thank You View attachment 22748
Might be easier to tie into the existing light instead of the switch. (ADD: or intercept the cable/conduit an any convenient point between the switch and the light) Electrically you are still tying onto the same two conductors.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Either as drawn or from the lighting outlet as kwired suggested. I would do whichever is more convenient as long as it doesn't exceed the box fill.
 