[B]Installation[/b] instructions are considered part of the UL Listing. All info added
by the manufacturer in addition to that required by UL must be in
compliance with NEC and UL standard. The UL standards used to
investigate and List products, contain specific requirements regarding the
content and appearance of the instructions. Installation instructions are not
required to be marked with the UL Mark, but they are required to be
provided with the product bearing the UL Mark. Some products are not
required to have installation instructions because the National Electrical
Code contains all the necessary installation requirements, such as outlet
boxes and various wiring methods. UL staff review the instructions, both in
the initial evaluation of the product, as well as during the continual
inspections at the factories. The clarity of the instructions is considered in
the review.
If there are questions regarding installation instructions, please contact
your Regulatory Services Representative.
4.7
(SW)
Q
I had a light installed in a shower. The manufacturers literature indicates
that it must have a GFCI installed. Is the GFCI required as a condition of
Listing or simply something that the manufacturer wanted to add
A
UL Listed Luminaires are evaluated for compliance with the Standard for
Luminaires, UL 1598. The UL Standard does not require GFCI protection
for luminaires used in the shower area. If the manufacturer chooses to
require GFCI protection in their installation instructions, then Section
110.3(B) of the NEC? would be applicable.