Wiring-up two legs of a 3-pole breaker

Status
Not open for further replies.

FaradayFF

Senior Member
Location
California
Hi Gents,
Do you see any issues with using a 3-phase breaker for an application where only one phase would be utilized? I have 1-phase, 208V load, but no spare 2 pole breakers.

Thanks,
EE
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
There are some low cost European style breakers out there that require you to loop power back through the 3rd pole, but those are not the type that are used here in panel boards and load centers. American designed breakers don’t care.
 