We're building apartments with heat pumps in each unit. Instead of installing disconnects at each HP we're moving the panels so they are with-in 50' and in sight of the HP. In one apartment, you can see the HP from the panel but if you were standing at the HP you can't see the panel. I read the definition in Article 100. Now when they say "equipment", are they talking about both the panel and HP???
 
Re: with-in sight

Yes

you can see the HP from the panel but if you were standing at the HP you can't see the panel.
Please correct me if I have missed something.
The disconnect means would need to be within sight of the motor controller of the HP, not the other way around, unless it is over 1/8hp, then a lockoff will do.

[ January 29, 2006, 11:48 PM: Message edited by: throttlebody ]
 
Re: with-in sight

Rule of thumb, an A/C or Heat Pump has about One Horse Power per Ton of Refrigeration. Also, 2 Tons is about the smallest A/C that is not window unit. So, the HP would be more than 1/8 horse. What I can't understand is, there are some "value" priced non fused disconnects that would make things a lot easier.
 
Re: with-in sight

Price is not the issue... appearance is. With the understanding electrical is suppose to be done correctly first ... appearance second... We're trying to avoid mounting a ugly disconnect in a living space. The panel could be moved. What throttle said is more of an answer I was looking for but he sounds unsure?.?.?.

Thnx for your replies.
 
Re: with-in sight

Originally posted by Shockedby277v:
We're trying to avoid mounting a ugly disconnect in a living space.
I get it now, you have a motel type "though-the-wall" unit.

If that is what you have, then those units are serviced from the front, by sliding the unit forward out of the frame. Try 440.63
 
Re: with-in sight

When you stated HP in each unit, I was thinking of the airhandler unit as what you were referring to. I wasn't sure though. I would not have guessed in was a "in wall" unit. Sorry.

If it is not an attachment plug assembly, you should still be able to use the overcurrent protection device if in a readily accessible location within sight of the unit.

440-65 would not apply if there is not a factory installed attachment plug.
 
Re: with-in sight

Originally posted by throttlebody:
440-65 would not apply if there is not a factory installed attachment plug.
Seen many without one? Not saying, just asking. I have never seen a PTAC without an attachment cord, unless it had a factory disconnect inside it.
 
Re: with-in sight

I have, but it has been more than 10 years ago, I paid no attention to if it had a disconnect inside as I was helping to get the jobsite caught up.(Hanging fixtures down the line :D

The statement about 440-65 was about the built in LCDI or AFCI requirements.
 