Hello everyone, as depicted in the image, there is a transformer positioned above a panel. The gap between the panel and the transformer measures 2 feet and 9 inches. Upon reviewing section 110.32, it appears that we require a clearance of at least 6 feet above the panel, is that correct? Furthermore, if the transformer were not present, the ceiling height remains insufficient at 6 feet.
Is it permissible for the transformer to be installed in this location?

Is it permissible for the transformer to be installed in this location?