This is a photo taken at an apartment building constructed in the 1960s. Was this actually allowed at the time? Panel over sink.jpg
 

Attachments

  • Panel over sink.jpg
    Panel over sink.jpg
    50.4 KB · Views: 5
Whoever put it there allowed it.

Other than working space, what is your objection.
Would you like to reach into a live panel while leaning against a presumably grounded stainless steel sink? :eek:
 
Mishandling that hose sprayer could shoot water directly up into that panel since it doesn't look like the door seats properly.
 
Code violation - working space in front of a panel must be from the floor to a minimum 7 ft. ceiling. No switches or receptacles are allowed in the wall behind a sink or cooktop, panels are not mentioned, but I think no inspector would allow it, even in the 1960s.
 