I guess I agree that it is, technically, a violation. But, I also feel that relocating this particular piece of equipment as well as the emergency circuit that feeds it is a waste of time and money. The required space to work on the panelboard safely can be achieved by simply rolling the piece of equipment out of the way. The AHJ is being a tad unreasonable. Imagine that.![]()
I often put panelboards in shallow closets with doors, that when opened provide adequate working clearance. That is similar to moving an object on wheels IMHO.
I often put panelboards in shallow closets with doors, that when opened provide adequate working clearance. That is similar to moving an object on wheels IMHO.
I respectfully disagree. Placing a panelboard in a shallow closet with the panelboard directly in front of the door is common and compliant in my opinion as long as the open door is as wide as the work space width required by 110.26. It would be impossible to access the panel with the door closed and it is unlikely the worker would close the door behind him or her before accessing the panel.
It must be. It doesn't even have to be on wheels. I come across that often any time I go to a service call. :rant::roll:
I'm curious to find out the REAL answer.
I agree with you, that's why I said ".... when opened provide adequate working clearance"
I often put panelboards in shallow closets with doors, that when opened provide adequate working clearance. That is similar to moving an object on wheels IMHO.