The NEC says that 3'-6" clearance is required for a 480V panel to any grounded parts table 110.26(A)(1) : Condition 2. Would grounded include the SIDE of a motor control center? I have a switchboard on one side of a room and a VFD on the other - both facing each other and both 480V. There is 20' between them. I would like to add a motor control center in the middle of the room facing one of the side walls. The MCC is 13' long - this leaves 3'-6" from the sides of the MCC to each of the VFD and switchboard faces. If the sides of the MCC are considered grounded then 3'-6" is fine if the sides of the MCC are considered exposed live parts then I need 4'. I am attaching a picture to describe the layout. Thanks in advance.