How about a few bollards out a little farther.
How about a few bollards out a little farther.
I had the same problem. Forklift drivers hit everything. I had to but bollards in front of drinking fountains edges of garage doors, electrical panels. etc.. Worse I had was a Gas heater tore off the ceiling. Had to evacuate the plant.
National Electrical Code 110.26 Spaces About Electrical Equipment states: ?
Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment. Enclosures housing electrical apparatus that are controlled by lock and key shall be considered accessible to qualified persons.
OSHA 29 1910.303 states: ? Working space about electric equipment. Sufficient access and working space shall be provided and maintained about all electric equipment to permit ready and safe operation and maintenance of such equipment.
Working clearances. Except as required or permitted elsewhere in this subpart, the dimension of the working space in the direction of access to live parts operating at 600 volts or less and likely to require examination, adjustment, servicing, or maintenance while alive may not be less than indicated in Table S-1. In addition to the dimensions shown in Table S-1, workspace may not be less than 30 inches wide in front of the electric equipment. Distances shall be measured from the live parts if they are exposed, or from the enclosure front or opening if the live parts are enclosed. Concrete, brick, or tile walls are considered to be grounded. Working space is not required in back of assemblies such as dead-front switchboards or motor control centers where there are no renewable or adjustable parts such as fuses or switches on the back and where all connections are accessible from locations other than the back. (continued)
TABLE S-1 - WORKING CLEARANCES
Minimum clear distance for condition(2) (ft)
Nominal voltage to ground (a) (b) (c)
0-150 (1)3 (1)3 3
151-600 (1)3 3 1/2 4
(1) Minimum clear distances may be 2 feet 6 inches for installations built prior to April 16, 1981.
(2) Conditions (a), (b), and (c), are as follows: (a) Exposed live parts on one side and no live or grounded parts on the other side of the working space, or exposed live parts on both sides effectively guarded by suitable wood or other insulating material. Insulated wire or insulated busbars operating at not over 300 volts are not considered live parts. (b) Exposed live parts on one side and grounded parts on the other side. (c) Exposed live parts on both sides of the workspace [not guarded as provided in Condition (a)] with the operator between.
Clear spaces. Working space required by this subpart may not be used for storage. When normally enclosed live parts are exposed for inspection or servicing, the working space, if in a passageway or general open space, shall be suitably guarded.
Access and entrance to working space. At least one entrance of sufficient area s hall be provided to give access to the working space about electric equipment.
Front working space. Where there are live parts normally exposed on the front of switchboards or motor control centers, the working space in front of such equipment may not be less than 3 feet.
Illumination. Illumination shall be provided for all working spaces about service equipment, switchboards, panelboards, and motor control centers installed indoors.
Headroom. The minimum headroom of working spaces about service equipment, switchboards, panel-boards, or motor control centers shall be 6 feet 3 inches.