Re: Working space
I?m not sure I understand the question. I wish I could post a sketch, but I?ll try a description.
Suppose that five enclosures (housing 102/208V components) are mounted side-by-side against the same wall. Looking down from above, you see that the backs of all five enclosures are in the same plane, as they are mounted on the same wall.
Now suppose that the first, third, and fifth enclosures are 24 inches deep. The second and fourth are 36 inches deep. So the front surfaces of all five are not in the same plane.
Finally, suppose that the available working clearance in front of the enclosures is 3 feet from the deeper enclosures, and therefore four feet in front of the shallower enclosures. I think that this example would represent the configuration described in the original question.
Here is my answer, in 2 parts:
</font>
- <font size="2" face="Verdana, Helvetica, sans-serif">If all the enclosures are all at least 30 inches wide, this is compliant.</font>
<font size="2" face="Verdana, Helvetica, sans-serif"></font>
- <font size="2" face="Verdana, Helvetica, sans-serif">If either of the shallower enclosures (number 2 or 4) is less wide than 30 inches, then you have a violation. That is because you need at least 30 inches of clear space, side-to-side, starting at the front edge of each enclosure, and because the deeper enclosure infringe on this space.</font>
<font size="2" face="Verdana, Helvetica, sans-serif">Does this answer your question?