Consider two electrical panels mounted catty-corner (that is, at 90 degrees in a corner) in an electrical room such that the 3-foot required clearance space of one is at right angles with and crosses the 3-foot clearance space of the other.
Since I am only looking at plans I can't tell in which direction the two doors open, so please consider two conditions. 1) When one of the panel doors is open it blocks the other one from being opened, or 2) when both panel doors are open the clearance spaces of both panels intersect.
Do either one of these conditions conflict with 110.26?
Look forward to your opinions,
Heinz R.
Since I am only looking at plans I can't tell in which direction the two doors open, so please consider two conditions. 1) When one of the panel doors is open it blocks the other one from being opened, or 2) when both panel doors are open the clearance spaces of both panels intersect.
Do either one of these conditions conflict with 110.26?
Look forward to your opinions,
Heinz R.