What depth of working space would be required for 277/480V switchgear that is mounted on one wall of an electrical room when 120V, grounded convenience receptacles are mounted on the opposite wall?
The definitions of "exposed (as applied to live parts)" and "live parts" in Article 100 leads me to believe that the contacts of the receptacle would cause this installation to fall under Table 110.26(A)(1), Condition 3, requiring the depth of the working space to be 4'-0". However, an associate has argued that because the 120V convenience receptacles are grounded, Condition 2 would apply and the working space would only be required to be 3'-6" deep.
Jason
The definitions of "exposed (as applied to live parts)" and "live parts" in Article 100 leads me to believe that the contacts of the receptacle would cause this installation to fall under Table 110.26(A)(1), Condition 3, requiring the depth of the working space to be 4'-0". However, an associate has argued that because the 120V convenience receptacles are grounded, Condition 2 would apply and the working space would only be required to be 3'-6" deep.
Jason