So I recently reconfigured an EE design su it would be more cost effective. Got 200a class j-fuses at the SES which run the MLO panelboards with typical QP 10,000kaic rated siemens breakers. I had to ask the engineer if for the panel AIC calcs as they need to be listed on the panels boards. One panel came in with high 35kaic rating. So I asked the EE if I need to install a MB with an AIC higher than this for safety and proper series rating.
His response to me was that I needed to check with the breaker manufacturer.
Shouldn’t I just tell home that I’m using siemens products x,y, and z and have him sign off that it’s safe. Isn’t this his job?
Below is the calcs he sent me and the manufacturer info. The way I read this, I need to add a QJ2H MB to panel A and then the combination with the j fuses and standard qp breakers would provide a 42kaic protection rating?
My supplier tells me I’m protected up to 100kaic bc that’s the rating of the SES fuses. I think he’s wrong. Give me your thoughts. Thx as always.