Went to a house and found ahot-tub wired like this--- from the main panel a 2p 50 breaker feeding with a 8-2 romex( through the attic and then to exterior wall then, sleeved in pvc down to a spa panel). The hot tub requires (1) 2p 20amp and (1) 2p 30amp circuit.. There is no neutral wire or additional ground rod!!!! Should I repull w/ 6-3 seperate the neutal/ground or do as my other journymal suggests and use the romex grd as a neutral and isolate the ground by driving a ground rod???? or put it back the way I found it??? GOTTA-GO play baseball w/youngen DENNIS
You do need to rewire it if the homeowner is willing to pay for a correct install, otherwise document what you have found as far as violations and give a copy to the homeowner and keep a copy for your records.
If the homeowner doesn't want to pay for the rewire see if they will at least give the name of whoever did the work in the first place and keep the name of the installer with the documentation.
This sounds like a typical handyman job to me and is the real reason I don't like to see handyman work, they tend to cut corners to keep the price down but never check to see what is required by code.
I have seen hot tubs installed by handymen cheaper than I can buy the materials to do the job correctly. There is no way to compete with that sort of work.