I am wiring this steam shower and the name plate saids to have 8awg wire pull on a 60amp breaker, I am confused, how is this correct???
If any trouble seeing the name plate pic late me know on the comments, thanks everyone


Sent from my iPhone using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The nameplate certainly skirts around the requirements of 110.14 or 334.80 and #8 NM certainly would not meet Code.

I supposed you could use a 90° conductor such as #8 THHN to a remote 90° termination point and then change over to a #6 NM.
 

new-master

Member
Location
MARYLAND
Occupation
ELECTRICIAN
Thank you, for the feed back,
My way was, pulled #6 romex and from this connect plan on going with greenfield or MC 8awg THHN
To comply with code