Would a switch wired too the load side of a GFCI trip the GFCI?

Status
Not open for further replies.
I am powering a single pole switch off the load side of a GFCI. The switch powers a very low amperage fluorescent fixture. Would turning the switch on trip the GFCI?
 

John120/240

Senior Member
Location
Olathe, Kansas
What kwired said. But does this light require GFCI protection for some reason ? Is the GFCI in another room from this fixture ?

If the GFCI feeds other receptacles & then trips, your light won't work thus causing trouble shooting head aches.
 

jeremysterling

Senior Member
Location
Austin, TX
I worked on some aquarium display flourescent lights that would trip the GFCI only when I used 2-lamp T8 GE instant start ballasts.

When I used a different manufacturer's ballast, I had no issues.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I have a fluorescent fixture in our bathroom that is on a GFCI, and a few of times a year, the GFCI will trip when you turn the light off.
 