bsmith8691
- Ellington, CT
I currently have an 8 floor apartment building. There are two three phase 120/208 owners panels that feed common areas with a common basement. The building was built and wired in 1963. I have a 1 inch rigid pipe run in the slab that goes directly from the panel to a 12 x 12 box in a utility closet. The conduit has 8 Branch circuits and three neutrals. I have a situation where phases A and C will trip when both of them are turned on. They work independently of each other. They feed LED stairwell lights and a Fob entry system. On a continuity check they do not ring phase to phase or phase to ground or phase to neutral. Because of the ampacity, at one point someone put three circuits on A phase and 3 circuits on C phase. I split each circuit and put it on its own breaker. I still have what appears to be a phase to phase short no matter how I split them up. Even if I take the circuit from A phase and put them on C phase and vice versa still trips. I have since put them on C phase in the tap box on a spare circuit coming from the panel. as they only draw 1.3 amps combined and haven't had any problems yet. Would anyone have any idea what in the world is going on?
Any and all help would be greatly appreciated.
Sent from my XT1254 using Tapatalk