My project manager told me that if I use a solid gray in use cover over top of an exterior GFCI receptacle it does not have to have the WR rating on it, apparently because the sun can’t get to it with a solid cover. I’ve looked around and can’t independently verify this. Do any of you know if this is true?


Sent from my iPhone using Tapatalk
 
My project manager told me that if I use a solid gray in use cover over top of an exterior GFCI receptacle it does not have to have the WR rating on it, apparently because the sun can’t get to it with a solid cover. I’ve looked around and can’t independently verify this. Do any of you know if this is true?


Sent from my iPhone using Tapatalk

They are required to be listed weather resistant type
406.9 (A)
2017 NEC
 
AFAIK the WR receptacles use the same plastic body as the non WR ones.

What is supposed to be different is the material the contact points are made of are supposed to be more corrosion resistant than the non WR receptacles.
 
Thanks, I appreciate the feedback. That’s my general conclusion as well but it’s nice to have a second opinion.