JFletcher
- Williamsburg, VA
Yes, it would, and given a difference in inductance of a factor of ten or more when the core is fully saturated, I suspect that it is possible.
And, of course, at full load the higher idling current would be adding (in quadrature) to the load current.
Also, the circulating currents if you connect the input wye point can easily be several times the full load current.
Both effects are bad.
If you apply, for example, 208 volts to one 120v wye winding the delta secondary will look a lot like a short circuit and so the resistive component of the idling current will be far greater than even the increased magnetizing current.
The delta winding will, in effect be trying to have L to L voltages of 480, 480, and 600. That triangle does not add up!
Isnt the high leg of a high leg delta that way because of the neutral being center tapped on the opposite two phases? If there is no neutral on the primary side, does a 240V high leg delta really differ from a straight 240V delta or even a theoretical 240/138Y service? L-L are all 240V.