Wye generator delta meter panel

FWD

Member
I have a 120/ 240 V. 3 phase 4 wire Delta service on a Sewer lift station . The customer ordered a 60 KW Generator factory connected Wye 120/208 V . The transfer switch is 3 pole with a solid neutral . I understand most 240 V equipment will run on 208 V , but is 120/208 V compatible with the incoming service with the un switched neutral ? Appreciate all replies , thank you .
 
There are 12 lead generators that can be reconfigured from 208Y/120 to 240/120 four wire delta...check and see if the generator is of that type.
 
  • Like
Reactions: FWD
I would not do this, even if it is a relatively small dedicated load that is not probably going to have future expansion.
Connecting a delta distribution system with a Wye source can be problematic without even getting into the voltage difference. For instance your grounded/ neutral conductor would now likely need to be counted as a current carrying conductor.

I do know some municipalities get away with it, especially with portable back up generators, bt why not just get the correct generator?
 
  • Like
Reactions: FWD
Do you already have the generator? If so post the make/model of the alternator. Is the generator hardwired to the output voltage or does it have a selector switch like the rental units have? (FYI I have a couple new (2-3hrs, couple years old, never installed regularly exercised) skid mount 65kva T4F generators if you need another :) )
 
  • Like
Reactions: FWD