No. This is not for academic discussion. Distribution Utility is multi grounded and their transformers are always grounded wye primary and secondary. I am wondering if they are considered separately derived system. What is the schematic diagram of a separately derived wye-grounded primary and wye grounded secondary?
They are not always wye and definitely not always grounded. The vast majority of transmission lines (115 kv and higher) are ungrounded. I haven’t even heard of one that is.
A lot of generating stations and in fact a lot of installations use either resistance grounded or ungrounded deltas or wyes precisely for the major fault current limitation and massive improvement in reliability particularly for MV subs and distribution.
Sure at the residential level they love their wye systems but that is not the norm everywhere.
And to the guy that said there is ALWAYS three two coil transformers, wrong again, even with utilities. If you have relatively small amounts of three phase loads it’s a common trick to use 2 transformers in an open delta, usually with one of them center grounded so the available voltages are 240/120 grounded single phase (Edison residential) and 240 high leg grounded delta but with a fairly high unbalanced impedance.
They are not as common but a lot of industrial customers request and often get delta-wye service due to its many advantages from their point of view.
Utilities though tend to do just one thing, over and over again. They are reluctant to do anything they are not familiar with so they tend to be very tribal in nature. With many of my customers being large industrials, Duke, Dominion, gas plants, water and waste water, and a lot of smaller independent producers especially, I see it all.