I did not say solidly grounded.Perhaps a nitpick , but not sure I like that phraseology, it's an oxymoron. I would leave out the"everything is grounded" part.
I did not say solidly grounded.Perhaps a nitpick , but not sure I like that phraseology, it's an oxymoron. I would leave out the"everything is grounded" part.
Perhaps "capacitively referenced to ground" would be a better way of putting it?I did not say solidly grounded.
It's a hack because the EGC is not the neutral and the inverter is required to measure line to neutral voltage. The NEC is pretty careful about making sure people don't use an EGC as a neutral, because it was not uncommon in decades past and a hazard. Technically, the inverter should have a neutral run to it, even if a reduced size neutral since it's not current carrying. In the way back days, inverters used to require a neutral to be run, then some bright bulb at an inverter company looked at a single line and thought, you know the neutral is in parallel with the EGC. We can tell installers they don't have to run a neutral if they connect a jumper between the ground and neutral terminals in the inverter and they will like that and buy more of our inverters. Of course once one manufacturer allowed this as an option then the others quickly followed.The SMA inverter data sheet plainly states that the service must be wye, but the output is balanced so there is no neutral current. Why is it a "hack" to strap the neutral to the EGC instead of running a conductor back to the service? Either way, it's only a voltage reference; there are lots of three phase inverters that allow this, and for SMA Tripower inverters it is the default.
Well, I guess that is one way to look at it, but it's a distinction without a difference. The NEC is made up of rules drawn up to prevent fires and injuries, and this method of voltage reference does not increase the probability of either.It's a hack because the EGC is not the neutral and the inverter is required to measure line to neutral voltage. The NEC is pretty careful about making sure people don't use an EGC as a neutral, because it was not uncommon in decades past and a hazard. Technically, the inverter should have a neutral run to it, even if a reduced size neutral since it's not current carrying. In the way back days, inverters used to require a neutral to be run, then some bright bulb at an inverter company looked at a single line and thought, you know the neutral is in parallel with the EGC. We can tell installers they don't have to run a neutral if they connect a jumper between the ground and neutral terminals in the inverter and they will like that and buy more of our inverters. Of course once one manufacturer allowed this as an option then the others quickly followed.
. In the way back days, inverters used to require a neutral to be run, then some bright bulb at an inverter company looked at a single line and thought, you know the neutral is in parallel with the EGC. .
Red electrons are attracted by the insulation and green electrons are repelled?... tell me again, what is it about the green dye in the insulation that the electrons and voltage measurement circuit don't like?
Pulling a neutral was not just annoying but a huge waste of resources, I wish that bright bulb figured out a way to do it without a ground reference at all but ill take what I can get. I always thought it was strange how VFD's (basically a type of inverter) never needed a neutral and those PV inverters did. VFD's are not without issue on delta banks, probably due to odd ground reference. I mean these things are basically computers now right ? They should be able to detect every oddball North American transformer configuration there ever was in 8 bits of memory.In the way back days, inverters used to require a neutral to be run, then some bright bulb at an inverter company looked at a single line and thought,
Surely the issue is that UL 1741 on grid-interactive inverters requires the inverter to confirm the grid configuration for both L-L and L-N voltages before the inverter can export power, so that's not possible.Pulling a neutral was not just annoying but a huge waste of resources, I wish that bright bulb figured out a way to do it without a ground reference at all but ill take what I can get.
A bit about terminology - if the service is grounded anywhere it is grounded everywhere, in the sense that the phase voltages are referenced to ground. It either is or it isn't. If the utility transformer is wye on the secondary side, the neutral is almost assuredly grounded at the transformer even if the neutral conductors are not run out of itr, which makes it a grounded wye. I hope that is what you have, but without looking at the transformer terminals, you can't tell; there certainly aren't any neutral conductors in those enclosures.GGunn, thanks for explaining that, ungrounded Wye now makes sense. Just the side that we (the customer or building electrical contractor) are seeing is ungrounded, but it is grounded at the service, right?
But I am afraid that is not what I am dealing with. The POCO meter tech was out there today, so I was able to look into the CT cabinet, no ground run from the utility transformer, just 6 sets of 3 phase conductors. He said it’s an open Delta service, ungrounded on any phase, and it looks that way to me. Only grounds are the groundING conductor bonding the steel raceway and enclosure. The utility (WE Energies) is slowly swapping factories over to Wye; they paid the customer side of a service rewire for a whole industrial park a few towns over. At the industrial park where I’ve been working on this job, they are slowly doing the same, but customers are footing the bill for new CT cabinets, wiring etc. I asked if he’d open the transformer for me, but said he didn’t have time, had to get to another job.
I got all 4 inverters working today (had communication and roof issues so failed last week,) they all show ~ 281 volts to ground, 490 phase to phase. But then turned them back off until we get inspection. Hopefully that inspection is next Monday, so am thinking I’ll just keep quiet about this til the inspection, discreetly confirm the service type with the utility engineer (the meter tech didn’t seem 100% sure) then if we need to install a Wye transformer it will be a “personal” issue. The other thing is that I’ve had them all working for a few hours now, so am tempted just to let them run and monitor the voltage (can do remotely on the inverter monitoring.)
I have one picture attached here of the groundING, going to follow up with a few posts of other pictures. I'm getting "to large of a file" message.
Thanks for your advice!
It's just the intended purpose. EGCs are for bonding to equalize potentials and to carry fault current in grounded systems. It's not that they can't do 5 other things, it's not that the EGC would not work as a current carrying conductor in place of a neutral. It's that it's not intended to be used for anything else. I've had to spend a lot of time explaining to people why on a single line diagram we have several conductors that are running in parallel that look like they could all do the same thing, carry electrons. Each has an intended purpose in the NEC.Well we are going to have to disagree. Having to run a neutral used to drive me absolutely crazy and. I was so glad when that ridiculousness stopped. And tell me again, what is it about the green dye in the insulation that the electrons and voltage measurement circuit don't like?
There are a very few inverters that can operate on an ungrounded service. It's got to be hard to design one that passes UL 1741 loss of phase detection or I'm sure there would be more. Taking ungrounded services, corner grounded deltas, and split phase deltas off the table probably does not reduce 3ph inverter sales all that much.Pulling a neutral was not just annoying but a huge waste of resources, I wish that bright bulb figured out a way to do it without a ground reference at all but ill take what I can get. I always thought it was strange how VFD's (basically a type of inverter) never needed a neutral and those PV inverters did. VFD's are not without issue on delta banks, probably due to odd ground reference. I mean these things are basically computers now right ? They should be able to detect every oddball North American transformer configuration there ever was in 8 bits of memory.
Clearly this is an example of a ungrounded 480V service, one of many many thousands of ungrounded systems in use. Hopefully the inverter manufacturers take notice that its not just 120/240, 208/120 and 480/277 out there. An inverter is supposed to be a 'smart' thing it should figure out that there is no neutral or L-N voltage reference.The POCO meter tech was out there today, so I was able to look into the CT cabinet, no ground run from the utility transformer, just 6 sets of 3 phase conductors. He said it’s an open Delta service, ungrounded on any phase, and it looks that way to me. Only grounds are the groundING conductor bonding the steel raceway and enclosure.
Well having to install costly transformers just because a manufacturer & UL can't match the service voltage is unacceptable. I hope the manufacturers can smell the coffee and work with the utilities to correct UL 1741 as we can clearly see its a enormous waste of resources to have idle transformer losses hours per day or any time the sun don't shine on all the thousands of solar systems that could be on some of the best roofs for solar, industrial roofs.Surely the issue is that UL 1741 on grid-interactive inverters requires the inverter to confirm the grid configuration for both L-L and L-N voltages before the inverter can export power, so that's not possible.
OK, well the first question is if there are inverters commercially available for ungrounded 480V deltas? If there are, then the issue is just that the OP selected the wrong inverter.Well having to install costly transformers just because a manufacturer & UL can't match the service voltage is unacceptable.