I was asked a question today I was not sure about.
Customer has a 3-phase 4-wire wye distribution system from the utility and generator to the ATS from the load of the ATS everything in this facility is 3-phase 3-wire. On his drawings it is state 3-phase 4-wire wye to the ATS and after the ATS the distribution is marked 3-phase 3-wire Delta.
While the utilization equipment may be Delta connected is the distribution properly designated Delta?