I have been asked to install a used air compressor.
350 hp
480v 3-phase
395 fla
12 lead
The compressor is supplied with a nema-5 and nema-6 starter and all required controls.ie ol's timers,etc.
The calculations I have done are as follows:
circuit breaker = 600 amp (414 fla x 150%=621)
conductor size= 700kcmil or parrallel 350's
conduit size = 2-2".
I also looked at section 440.32 and found a 72% derating factor. Does this apply?
SEE ATTACHMENT.