hhsting
- Glen bunie, md, us
- Junior plan reviewer
Attached sketch shows from left to right: 600VAC inverters feeding customer owned 600V, 3000A service rated switchboard which has neutral to ground bond, GEC to ground grid and feeds 2000kVA 600VAC to 13.2kVAC customer owned transformer wye to wye. The transformer has no neutral to ground bond but has GEC to ground grid and bonding jumper from 600VAC switchboard goes to transformer gnd bar. The transformer then feeds via (3)#1 AWG 15kv MV-90 with concentric neutral to 15kV customer owned switchgear 125A fuses disconnect. The point of interconnection is shown in sketch after the 125A fuses in15kV switchboard. Their is bonding jumper from transformer to 15kV switchboard #1 AWG GND and their is again GEC from 15kV swbd to ground grid.
2000kVA transformer and 600 VAC are on one pad and 15kV swithboard is on separate pad next to each other.
There is also 600V to 240/120V, 5kVA transfromer fed from 600 VAC Swbd which feeds receptacle and 15kV switchboard space heaters either 120V or 240V single phase.
I have following questions and am really confused:
1. Does the 2000kva transformer 13.2kV side wye has to have system bonding jumper bonding neutral to gnd? If yes then how does that work in transformer or at the 15kV SWBD?
2. Does their need to be neutral to bond at 15kV SWBD 125A fuses since that would be service disconnect?
3. One neutral to bond exists at 600VAC Swbd attached sketch shown does it need any other neutral to bond by code anywhere or need to be relocated? Not sure how this would work. Everything is customer owned.
4. Concentric neutral to transfromer would you need actual separate neutral from 15kV Swbd to 2000kva transfromer or concentric is ok per code?
5. 5kVA 600VAC to 240/120VAC single phase transformer too much fed from 600VAC switchboard? Should it be their by code.
All reference NEC 2014 code please not in other versions of code yet.