I like the sketch but in Option B there is a bond from H0/Xo terminal in the LV side to the ground pad.
that should be clearly shown in the sketch.
as synchro and others have pointed out
we need that for fault clearing and to comply with 250.4(A)(5) and 250.122.
The question becomes does 250.184(C)(1) allow it?
250.184 modifies 250.24(A)(5) and
250.142(B).
In post #132
I agree its murkey but as soon as you hit 250.180 code is modified including the entire transformer.
The demarcation is noted on the option B drawing.
The H0/X0 --> G connection is in the 'transformer' and is allowed on either side.
As option B shows in the sketch.
http://thinkelectric.org/continuingEd/wye-wye2.pdf
All the 'ground pads' in the transformer do get bonded together within the transformer.
[I should add the pass thru ground pad on the HV side and the three concentric.]
All references 2014 NEC
that should be clearly shown in the sketch.
as synchro and others have pointed out
we need that for fault clearing and to comply with 250.4(A)(5) and 250.122.
The question becomes does 250.184(C)(1) allow it?
250.184 modifies 250.24(A)(5) and
250.142(B).
250.180 General. Where systems over 1000 volts are grounded,
they shall comply with all applicable provisions of the preceding
sections of this article and with 250.182 through 250.194, which
supplement and modify the preceding sections.
250.184(C) Multigrounded Neutral Systems. Where a multigrounded
neutral system is used, the following shall apply:
(1)The neutral conductor of a solidly grounded neutral system
shall be permitted to be grounded at more than one point.
Grounding shall be permitted at one or more of the fol-
lowing locations:
a. Transformers supplying conductors to a building or
other structure
I addressed exactly this point in post #132
In post #132
MGN only applies to MV. So you are into a game of where you ground the neutral and where that point of demarcation is.
I agree its murkey but as soon as you hit 250.180 code is modified including the entire transformer.
The demarcation is noted on the option B drawing.
The H0/X0 --> G connection is in the 'transformer' and is allowed on either side.
As option B shows in the sketch.
http://thinkelectric.org/continuingEd/wye-wye2.pdf
All the 'ground pads' in the transformer do get bonded together within the transformer.
[I should add the pass thru ground pad on the HV side and the three concentric.]
All references 2014 NEC